The following tables list and describe the parameters specific to the UIS command component types for this remote device:
For more general information about UIS command component parameters, see UIS Command Components. The DG_F_DEV (Get data group from device) and DG_T_DEV (Send data group to device) command component types are configured in the template file. The other command component types are considered ‘special’ and are defined in the EIE editor code. See Special UIS Command Component Types for more information.
Clear All History Tx Info clears all historical data group caches. CLRHSTXA has no command parameters.
Note: If you clear all caches using a UIS command, the cache values in each transaction of historical data groups are not reset; past transactions continue to display actual values. This is done for performance reasons so that each DDS transaction does not have to be updated. The driver ignores these cached values after the command has been issued.
Get RTU Configuration retrieves configuration information from the field device. CONFIG has no parameters.
|
Update CygNet Point updates the record for a CygNet point. CYUPDTPT has the following command parameters:
|
|
Wait for CygNet Point signals the UIS to wait to perform a command until the value of the specified CygNet point changes to a specified value. CYWAITPT must be the first command component added to a UIS command. You cannot add other instances of CYWAITPT to a UIS command. CYWAITPT has the following command parameters:
|
Get data group from device retrieves a data group from a field device. The Parent XML Element is uccRecvParms. The following parameters are available for each specified data group type.
| Data Group Type | Parameter | Required | Description |
|---|---|---|---|
|
EDate |
No |
Ending Contract Date defines the ending contract time and date for a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
SDate |
No |
Starting Contract Date defines the starting contract time and date for a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
Date |
Yes |
History Date defines the date and time of a daily (24-hour) archive request. Value options are strings in formats described in Selecting Date and Time. |
|
|
ClearLog |
Clear Audit Log defines whether or not to clear events after retrieving them. Clearing an event causes it to be marked as cleared in the device, but does not delete the event. Value options are Boolean. Note: This parameter is not available for 107IC devices. |
||
|
EDate |
Ending Contract Date defines the ending contract time and date for a date-range request. Value options are strings in formats described in Selecting Date and Time. |
||
|
GetUC |
Get Uncleared Audit Records defines whether or not to retrieve all audit records not previously cleared. Value options are Boolean. Note: This parameter is not available for 107IC devices. |
||
|
SDate |
Starting Contract Date defines the starting contract time and date for a date-range request. Value options are strings in formats described in Selecting Date and Time. |
||
|
Cnt |
Yes |
Number of Locations defines the number of table entries to include in the "Configurable Opcode Data" data group. Value options are integers from 1 to 44. |
|
|
Val1 |
Yes |
Starting Location defines which table entry to begin with when generating table entries for the "Configurable Opcode Data" data group. Value options are integers from 1 to 44. |
|
|
EDate |
No |
Ending Contract Date defines the ending contract time and date for a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
SDate |
No |
Starting Contract Date defines the starting contract time and date for a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
EDate |
Yes |
Ending Date and Time defines the ending date and time
of a date-range request for extended history.
Value options are strings in formats described in Selecting Date and Time. |
|
|
GetLatest |
No |
Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache). Value options are Boolean. For more information, see History Retrieval Optimization. |
|
|
SDate |
Yes |
Starting Date and Time defines the starting date and time of a date-range request for extended history. Value options are strings in formats described in Selecting Date and Time. |
|
|
EDate |
Yes |
End Device Date/Time defines the ending device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
SDate |
Yes |
Start Device Date/Time defines the starting device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
ClearLog |
No |
Clear Audit Log defines whether or not to clear events after retrieving them. Clearing an event causes it to be marked as cleared in the device, but does not delete the event. Value options are Boolean. Note: This parameter is only available for 300IC and 400IC devices. |
|
|
EDate |
Yes |
End Device Date/Time defines the ending device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
GetUC |
No |
Get Uncleared Audit Records defines whether or not to retrieve all audit records not previously cleared. Value options are Boolean. Note: This parameter is only available for 300IC and 400IC devices. |
|
|
SDate |
Yes |
Start Device Date/Time defines the starting device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. |
|
|
EDate |
Yes |
End Device Date/Time defines the ending device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. Note: This parameter is only available for 107 and 107IC devices. |
|
|
SDate |
Yes |
Start Device Date/Time defines the starting device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. Note: This parameter is only available for 107 and 107IC devices. |
|
|
EDate |
Yes |
End Device Date/Time defines the ending device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. Note: This parameter is only available for 107 and 107IC devices. |
|
|
SDate |
Yes |
Start Device Date/Time defines the starting device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. Note: This parameter is only available for 107 and 107IC devices. |
|
|
EDate |
Yes |
End Device Date/Time defines the ending device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. A maximum of 16 characters may be used. |
|
|
SDate |
Yes |
Start Device Date/Time defines the starting device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. A maximum of 16 characters may be used. |
|
|
EDate |
Yes |
End Device Date/Time defines the ending device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. Value options are strings in formats described in Selecting Date and Time. |
|
|
SDate |
Yes |
Start Device Date/Time defines the starting device date and time of a date-range request. Value options are strings in formats described in Selecting Date and Time. Value options are strings in formats described in Selecting Date and Time. |
|
|
EDate |
Yes |
Ending Date defines the ending date and time of a date-range request for row-based daily history for multiple points. Value options are strings in formats described in Selecting Date and Time. |
|
|
GetLatest |
No |
Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache). Value options are Boolean. For more information, see History Retrieval Optimization. |
|
|
NumHistPt |
Yes |
Number of Hist Pts defines the number of history points to be retrieved. Value options are integers from 1 to 100, which is the maximum number of history points in the segment. The combination of Starting Hist Pt and Number of Hist Pts should not exceed 100. |
|
|
SDate |
Yes |
Starting Date defines the starting date and time of a date-range request for row-based daily history for multiple points. Value options are strings in formats described in Selecting Date and Time. |
|
|
StHistPt |
Yes |
Starting Hist Pt defines the beginning of the range of history points to be retrieved. Value options are integers from 1 to 100, which is the maximum number of history points in the segment. |
|
|
EDate |
Yes |
Ending Date defines the ending date and time of a date-range request for row-based extended history for multiple points. Value options are strings in formats described in Selecting Date and Time. |
|
|
GetLatest |
No |
Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache). Value options are Boolean. For more information, see History Retrieval Optimization. |
|
|
NumHistPt |
Yes |
Number of Hist Pts defines the number of extended history points to be retrieved. Value options are integers from 1 to 50, which is the maximum number of extended history points. The combination of Starting Hist Pt and Number of Hist Pts should not exceed 50. |
|
|
SDate |
Yes |
Starting Date defines the starting date and time of a date-range request for row-based extended history for multiple points. Value options are strings in formats described in Selecting Date and Time. |
|
|
StHistPt |
Yes |
Starting Hist Pt defines the beginning of the range of extended history points to be retrieved. Value options are integers from 1 to 50, which is the maximum number of extended history points. |
|
|
EDate |
Yes |
Ending Date defines the ending date and time of a date-range request for row-based periodic history for multiple points. Value options are strings in formats described in Selecting Date and Time. |
|
|
GetLatest |
No |
Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache). Value options are Boolean. For more information, see History Retrieval Optimization. |
|
|
NumHistPt |
Yes |
Number of Hist Pts defines the number of history points to be retrieved. Value options are integers from 1 to 100, which is the maximum number of history points in the segment. The combination of Starting Hist Pt and Number of Hist Pts should not exceed 100. |
|
|
SDate |
Yes |
Starting Date defines the starting date and time of a date-range request for row-based periodic history for multiple points. Value options are strings in formats described in Selecting Date and Time. |
|
|
StHistPt |
Yes |
Starting Hist Pt defines the beginning of the range of history points to be retrieved. Value options are integers from 1 to 100, which is the maximum number of history points in the segment. |
|
|
EDate |
Yes |
Ending Date defines the ending date and time of a date-range request for periodic history. Value options are strings in formats described in Selecting Date and Time. |
|
|
GetLatest |
No |
Get Latest? defines whether or not to retrieve history from the latest successfully read history record (the cache). Value options are Boolean. For more information, see History Retrieval Optimization. |
|
|
SDate |
Yes |
Starting Date defines the starting date and time of a date-range request for periodic history. Value options are strings in formats described in Selecting Date and Time. |
|
|
DataType |
Yes |
Data Type defines the type of data stored at the specified register number. Value options appear in the Data Type drop-down menu in the Single Register data group dialog box. |
|
|
FacUdc |
No |
Facility.UDC for Point Processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT). Value options are strings that specify a Facility.UDC combination. |
|
|
TLP |
Yes |
T,L,P (one-based) defines the Point Type, Logical, Parameter combination to be retrieved from the device. Value options are integers, separated by commas, in the form T,L,P. The Point Type (T) portion of the value can be any valid point type on the device. The Logical (L) portion of the value is one-based and can be any valid logical for the specified point type. The Parameter (P) portion of the value can be any valid parameter of the specified point type. |
|
|
TLPDesc |
No |
TLP Description provides for a user-defined description of the TLP in the event that the user does not want to use the default description. Value options are alphanumeric characters. |
|
|
Cnt |
No |
Number of Data Items defines the total number of data items retrieved for a soft point request. Total number does not include soft point tag or integer flag. Value options are integers 1 - 20. |
|
|
Item |
No |
Starting Data Item # defines the soft point data item number from which to begin retrieving soft points. This does not include soft point tag or integer flag. Value options are integers 1 - 20. |
Send data group to device sends a data group to a field device. The parent XML Element is uccSendParms. The following parameters are available for each specified data group type.
| Data Group Type | Parameter | Required | Description |
|---|---|---|---|
|
Val1 |
Yes |
Output Value in EUs enables you to set the analog output engineering unit value. Value options are floating-point numbers. |
|
|
WrtCfgMem |
Yes |
Write to config memory flag indicates whether to write to config memory. |
|
|
Item |
Yes |
Table Item # defines which table entry a value is sent to in a "Configurable Opcode Data" data group. Value options are integers 1 - 44. |
|
|
Value |
No |
Value defines a value to be sent to a "Configurable Opcode Data" data group. Value options are determined by the table entry type and may be integer, string, or others. |
|
|
Val1 |
No |
Status defines the actual value that is written to the digital output. Value options are Boolean. The value determines whether the device sets the output line high or low. |
|
|
Val2 |
No |
TDO EU Value enables you to set the timed discrete output engineering unit value. Value options are floating-point numbers. |
|
|
AccLevel |
No |
Access Level defines the security access level assigned to the corresponding operator ID. Value options are char values 0 - 5. |
|
|
OpID |
Yes |
Operator ID defines the identifier of an operator. Value option is a user-defined string. |
|
|
Password |
No |
Password defines the password assigned to the corresponding operator ID. Value options are integers from 0 - 9999. |
|
|
DataLen |
No |
String Length specifies the string length of data stored at the specified register number. |
|
|
DataType |
Yes |
Data Type defines the type of data stored at the specified register number. Value options appear in the Data Type drop-down menu in the Single Register data group dialog box. |
|
|
FacUdc |
No |
Facility.UDC for Point Processing provides a means to specify a UDC to which to map the specified data point; it requires a corresponding point in the Point Service (PNT). Value options are strings that specify a Facility.UDC combination. |
|
|
TLP |
Yes |
T,L,P (one-based) defines the Point Type, Logical, Parameter combination to be retrieved from the device. Value options are integers, separated by commas, in the form T,L,P. The Point Type (T) portion of the value can be any valid point type on the device. The Logical (L) portion of the value is one-based and can be any valid logical for the specified point type. The Parameter (P) portion of the value can be any valid parameter of the specified point type. |
|
|
TLPDesc |
No |
TLP Description provides for a user-defined description of the TLP in the event that the user does not want to use the default description. Value options are alphanumeric characters. |
|
|
Value |
Yes |
Value defines the value of the TLP. |
|
|
Item |
Yes |
Data Item # defines the number of the soft point data item to be sent to the field device. Value options are integers 1 - 20. |
|
|
Value |
Yes |
Value defines the value for the corresponding soft point data item to be sent to the field device. Value options are floats. |
|
|
ContHr |
Yes |
Contract Hour defines the contract hour to be sent to a field device for system variables. Value options are integers 0 - 23. |
Get RTU Time retrieves time from the field device. GETTIME has no command parameters.
Set RTU Time sets time for the field device. SETTIME has no command parameters.
Get Current Status retrieves current status from the field device. STATUS has no command parameters.
Note: The Get Current Status UIS command is not available for Emerson FBx devices.