Devices > Remote Devices > Device Template Files > Elements and Attributes > block

block

The blockn element defines constraints used to map register data to data group elements (DataGroupElement) within a CygNet data group. Each block defines a structure that reads or writes contiguous registers. Multiple blocks can be used, depending on the requirements of the dependent data group(s). CygNet blocks are not restricted by the Modbus maximum message size of 250 data bytes; you can specify any number of contiguous registers to retrieve per block when using the regCnt attribute.

The first block is always block1. Subsequent blocks are blockn, where n represents the block number. Blocks must be enumerated consecutively; block enumerations can only be used once. So if you use three blocks, call the blocks block1, block2, and block3. Fewer blocks means fewer communication transactions between the CygNet host and field device(s). It might be more efficient for you to use fewer blocks and bring back extra bytes than to create numerous blocks with few bytes.

To read to or write from a single register, either define only one data element in the applicable data group or use a single-element data group.

This element is:

To learn about how this element relates to other elements in a CygNet device template file, see Template File Hierarchy.

Example

Attributes

The following table lists and describes attributes generally applicable to this element. However, not all of the attributes listed here are applicable to all EIEs. Additionally, some attributes are required for use in every device template file of a certain EIE, but others may be used on a case-by-case or device-by-device basis, depending on your specific needs. All attributes in templates are case sensitive; but the case sensitivity of attribute values is based on context.

Note: Occasionally, device template files for different EIEs use attributes of the same name that do different things. Efforts are made in this document to highlight cases where an attribute by one name does different things in different EIEs.

Attribute Description

cardIncrement

cardIncrement specifies a number of registers by which to increment when multiple dynagraph cards are available. The number of cards supported for each card type is defined by protocol.

Value:
  • Must be a positive whole number.

cardRep

cardRep specifies the type of DynaCard data represented by a card or block element.

Value:
  • Must be defined at the card or block level for every block included in a card element.
  • downhole: Indicates that the data source is downhole. If set to downhole, downholePtCount must also be defined in the parent or grandparent element.
  • none: Indicates that the data source is neither downhole nor surface.
  • surface: Indicates that the data source is surface. If set to surface, surfacePtCount must also be defined in the parent or grandparent element.

funcCode

funcCode specifies the Modbus function code for accessing a register or block of registers.

Value:
  • Must be a positive whole number.
  • Must be a valid and supported Modbus function code.

See Function Codes.

len

len specifies the number of bytes in a data group element or register.

Value:
  • Must be a positive whole number.

newTx

newTx specifies that a new message transaction starts at the block element in which newTx is defined and includes block data for all subsequent blocks until another definition of newTx set to true is encountered.

Value:
  • Must be a Boolean value true or false.

ordIncrement

ordIncrement specifies how many registers make up an increment of registers. It is always used in combination with regNum, which specifies a starting register number from which to increment.

These two attributes are used to specify one or more groups of registers that correspond to data group ordinals. ordIncrement always depends on regNum, but regNum does not depend on ordIncrement. Optionally, use regNum_ordn in place of ordIncrement + regNum.

Value:
  • Must be an integer.

regBitLen

regBitLen specifies the length in bits of each register returned from the device for the specified funcCode. This setting can change from section to section and from register to register in the device. Refer to field device documentation for these settings.

Value:
  • Must be a positive whole number.

Modbus coil data groups using function code 1, 2, 5, or 15 must use regBitLen, not regByteLen.

See also regByteLen.

regByteLen

regByteLen specifies the length in bytes of each register returned from the device for the specified funcCode. This setting can change from section to section and from register to register in the device. Refer to field device documentation for these settings.

Value:
  • Must be a positive whole number.

Modbus coil data groups using function code 1, 2, 5, or 15 must use regBitLen, not regByteLen.

See also regBitLen.

regCnt

regCnt specifies the number of registers to be returned in a block. CygNet blocks are not restricted by the Modbus maximum message size of 250 data bytes; you can specify any number of contiguous registers to retrieve per block when using the regCnt attribute.

Value:
  • Must be a positive whole number.

regNum

regNum defines a starting register number.

To make this attribute meter specific, append _ordn to the attribute. For example, regNum_ord1.

To define a logical register number, as with Modbus devices, use regNum in conjunction with regOff.

To make this attribute request-type specific for use in DynaCard preCard and/or postCard elements, append _singleCard or _multipleCard to the attribute. For instance, regNum_singleCard. regNum without the appendix cannot be used in the same element as regNum_singleCard or regNum_multipleCard. If you use _singleCard or _multipleCard, you must also use the other in the same block element.

Value:
  • Must be a positive whole number.

regOff

regOff defines a register offset that translates a logical register number into a physical register number. It is always used in conjunction with regNum. It may be defined in the same element as regNum, or it may be defined in a parent element then inherited by one or more regNum attributes.

regOff enables you to translate Modbus coil/register numbers into data addresses used by field devices. Modbus coil/register numbers are not the same thing as data addresses. For example, the Modbus register number 30001 typically uses the data address 0, which means that you would want to offset a regNum value of 30001 by -30001 in order to return a data address of 0 (or 0x0000).

Typical offset constants are as follows:

  • -1
  • -10000, -10001
  • -30000, -30001
  • -40000, -40001

You must consider the Modbus coil/register range convention you follow and the data addressing convention you follow. In both cases, know the range starting number and the extent of the range. The offset can be determined from the field device manual or register map.

Value:
  • Must be an integer.

toDevice

toDevice specifies that a block element first writes a value to a field device before the rest of a read message is executed. Used when a specification must be sent before the field device "knows" what to load and return.

Value:
  • Must be a Boolean value true or false.

txMaxRegCnt

txMaxRegCnt specifies the maximum number of registers that may be communicated in a single transaction. This attribute is optional and intended to provide a way to make messages for a single block smaller than the Modbus maximum message size of 250 data bytes. How many registers you read or write within byte constraints depends on the size of the registers with which you are communicating.

txMaxRegCnt is used in conjunction with the regCnt attribute. regCnt specifies the number of registers to be returned in a single block; txMaxRegCnt merely constrains the size of the message(s) used to communicate registers. For example, if you want to retrieve 125 2-byte registers in a single message, set regCnt to 125 and do not use txMaxRegCnt. But if you want to retrieve 125 2-byte registers in five messages, set regCnt to 125 and txMaxRegCnt to 25.

Value:
  • Must be a positive whole number.
  • Cannot exceed the number of registers that the Modbus maximum message size of 250 data bytes can accommodate.

type

type defines the appropriate data type for one or more DataGroupElement elements; it can be inherited from a parent element.

Value:
  • bin.hex: Binary hex
  • boolean: Boolean
  • i1: Character
  • i2: Short integer
  • i4: Integer
  • i8: Integer
  • r4: Float
  • r8: Double
  • ui1: Byte
  • ui2: Unsigned short integer
  • ui4: Unsigned integer
  • ui8: Unsigned integer
  • string: String
  • struct: Structure

See also sourceType.

Function Codes

The following Modbus function codes are supported by CygNet.

Code Name Description

1

Read Coils

Reads contiguous coil statuses from 1 - 2000. Registers must be read-only Boolean.

2

Read Discrete Inputs

Reads contiguous discrete input statuses from 1 - 2000. Registers must be read/write Boolean.

3

Read Holding Registers

Reads contiguous contents of a block of holding registers. Registers must be read-only 16 or 32 bit.

4

Read Input Registers

Reads contiguous input registers from 1 - 125. Registers must be read/write 16 or 32 bit.

5

Write Single Coil

Writes ON or OFF to a single coil. Registers must be read/write Boolean.

6

Write Single Register

Writes data to a single holding register. Register must be 16 or 32 bit.

7

Read Exception Status

Reads the contents of eight exception status outputs in a remote device.

15

Write Multiple Coils

Writes ON or OFF to multiple coils in sequence. Registers must be Boolean.

16

Write Multiple Registers

Writes data to a block of contiguous registers from 1 - 123. Registers must be 16 or 32 bit.