FMS Validation Rules
The CygNet measurement system contains several categories and types of validation rules. Rules are assigned to validation engines, where they comprise a set of checks against the data for a single associated Node. Each rule can be configured to automatically detect potential problems in your data, according to its configured limits and guidelines. The system processes normalized data for validation rules as it applies to the given data type. Data will be validated by device rules first, and then all other applicable rules will follow.
When configuring rule properties, you can name or rename the rule as desired. If you do not assign a rule name, it will retain the default rule name based on the rule type, as listed in the tables below. Multiple rules in a validation engine can have the same name, although you may want to assign unique names upon rule creation to more easily identify them. See Configuring Validation Rules for more information.
Validation Rule Categories
Validation rules are organized into the following categories, based on affected data types. For each category, available rule types are listed in the corresponding tables below.
- Configuration Data
- Gas Quality History
- Periodic Metering History
- Historical Data
- Station
- Gas Analysis Data
- Job
See Managing Validation Engines for information about defining validation engines and their associated Nodes.
Configuration Data Rules
The following table lists the available validation rule types for a single configuration record, and each rule's configuration options. Configuration data validation is currently supported for gas device Nodes.
Gas Quality History Rules
The following table lists the available validation rule types for gas quality data from live history records, and each rule's configuration options. These rules will be validated against live gas history data on Nodes that support gas quality data.
| Rule Type | Default Rule Name | Valid Node Categories | Description | Configuration Options |
|---|---|---|---|---|
|
Gas Composition Normalization (Percentage) |
Gas Comp Norm |
Gas Device Liquid Device |
The system will validate that the gas composition adds up to 100% within the specified tolerance. Records failing validation will generate an exception. |
Specify the Severity, Data quality, and a +/- percentage range for the tolerance |
|
Sum Tolerance... validation rules: The system will validate that the sum of the components is within the specified tolerance. |
||||
|
Sum of CO2, N2 (Percentage) |
Sum of CO2, N2 |
Gas Device |
The system will validate that the sum of the CO2 and N2 components are within the specified tolerance. Records failing validation will generate an exception. |
Specify the Severity, Data quality, and a Low and High percentage value for the tolerance |
|
Sum of iC5, nC5, C6 (Percentage) |
Sum of iC5, nC5, C6 |
Gas Device |
The system will validate that the sum of the iC5, nC5, and C6 components are within the specified tolerance. Records failing validation will generate an exception. |
Specify the Severity, Data quality, and a Low and High percentage value for the tolerance |
Periodic Metering History Rules
The following table lists the available validation rule types for periodic metering history data, and each rule's configuration options.
Historical Data Rules
The following table lists the available validation rule types for previously retrieved (historical) multiple gas quality or periodic metering data records, and each rule's configuration options.
| Rule Type | Default Rule Name | Valid Node Categories | Description | Configuration Options |
|---|---|---|---|---|
|
Average... validation rules (gas devices): The system will validate that the reported data does not deviate outside historical averages for the specified number of previous records. |
||||
|
Average - Diff Pressure (Absolute) |
Avg DP Abs |
Gas Device |
The system will validate that the reported data does not go outside a defined range of historical averages for the specified number of previous records. Records failing validation will generate an exception. Note: Differential Pressure values of null or zero (0) will not trigger exceptions.
|
Specify the Severity, Data quality, a +/- absolute/percentage range, the last # of records to consider, and Units to use (for absolute rules) See Notes below.
|
|
Average - Diff Pressure (Percentage) |
Avg DP Pct |
Gas Device |
||
|
Average - Energy (Absolute) |
Avg Energy Abs |
Gas Device |
||
|
Average - Energy (Percentage) |
Avg Energy Pct |
Gas Device |
||
|
Average - Mass (Absolute) |
Avg Mass Abs |
Gas Device |
||
|
Average - Mass (Percentage) |
Abs Mass Pct |
Gas Device |
||
|
Average Static Pressure (Absolute) |
Avg SP Abs |
Gas Device |
||
|
Average - Static Pressure (Percentage) |
Avg SP Pct |
Gas Device |
||
|
Average - Temperature (Absolute) |
Avg Temp Abs |
Gas Device |
||
|
Average - Temperature (Percentage) |
Avg Temp Pct |
Gas Device |
||
|
Average - Volume (Absolute) |
Avg Vol Abs |
Gas Device |
||
|
Average - Volume (Percentage) |
Avg Vol Pct |
Gas Device |
||
|
Average... validation rules (liquid devices): The system will validate that the device data does not deviate outside historical averages for a specified number of previous records. |
||||
|
Average - Accumulated Energy (Absolute) |
Avg Accm Energy Abs |
Liquid Device |
The system will validate that the reported data does not go outside a defined range of historical averages for the specified number of previous records. Records failing validation will generate an exception.
|
Specify the Severity, Data quality, a +/- absolute/percentage range, the last # of records to consider, and Units to use (for absolute rules) See Notes below.
|
|
Average - Accumulated Energy (Percentage) |
Avg Accm Energy Pct |
Liquid Device |
||
|
Average - Base Density (Absolute) |
Avg Base Dens Abs |
Liquid Device |
||
|
Average - Base Density (Percentage) |
Avg Base Dens Pct |
Liquid Device |
||
|
Average - Density Pressure (Absolute) |
Avg Dens Prss Abs |
Liquid Device |
||
|
Average - Density Pressure (Percentage) |
Avg Dens Prss Pct |
Liquid Device |
||
|
Average - Density Temperature (Absolute) |
Avg Dens Temp Abs |
Liquid Device |
||
|
Average - Density Temperature (Percentage) |
Avg Dens Temp Pct |
Liquid Device |
||
|
Average - Gross Standard Volume (Absolute) |
Avg Grs Std Vol Abs |
Liquid Device |
||
|
Average - Gross Standard Volume (Percentage) |
Avg Grs Std Vol Pct |
Liquid Device |
||
|
Average - Gross Volume (Absolute) |
Avg Gross Vol Abs |
Liquid Device |
||
|
Average - Gross Volume (Percentage) |
Avg Gross Vol Pct |
Liquid Device |
||
|
Average - Indicated Volume (Absolute) |
Avg Ind Vol Abs |
Liquid Device |
||
|
Average - Indicated Volume (Percentage) |
Avg Ind Vol Pct |
Liquid Device |
||
|
Average - Mass (Absolute) |
Avg Mass Abs |
Liquid Device |
||
|
Average - Mass (Percentage) |
Avg Mass Pct |
Liquid Device |
||
|
Average - Meter Pressure (Absolute) |
Avg Meter Prss Abs |
Liquid Device |
||
|
Average - Meter Pressure (Percentage) |
Avg Meter Prss Pct |
Liquid Device |
||
|
Average - Meter Temperature (Absolute) |
Avg Meter Temp Abs |
Liquid Device |
||
|
Average - Meter Temperature (Percentage) |
Avg Meter Temp Pct |
Liquid Device |
||
|
Average - Net Standard Volume (Absolute) |
Avg Net Std Vol Abs |
Liquid Device |
||
|
Average - Net Standard Volume (Percentage) |
Avg Net Std Vol Pct |
Liquid Device |
||
|
Average - Observed Density (Absolute) |
Avg Obs Dens Abs |
Liquid Device |
||
|
Average - Observed Density (Percentage) |
Avg Obs Dens Pct |
Liquid Device |
||
|
Average - Sediment and Water Volume (Absolute) |
Avg S&W Vol Abs |
Liquid Device |
||
|
Average - Sediment and Water Volume (Percentage) |
Avg S&W Vol Pct |
Liquid Device |
||
|
Average - Uncorrected Density (Absolute) |
Avg Uncorr Dens Abs |
Liquid Device |
||
|
Average - Uncorrected Density (Percentage) |
Avg Uncorr Dens Pct |
Liquid Device |
||
|
Frozen Value... validation rules (gas devices): The system will validate that a device is not incorrectly reporting the same value for a specified number of records. A device repeatedly reporting the same value will be considered frozen. |
||||
|
Frozen Value - Diff Pressure (Absolute) |
FrzVal DP Abs |
Gas Device |
The system will validate that the reported data remains within a defined tolerance range for the specified number of records to be considered frozen. Records failing validation will generate an exception. Note: Differential Pressure values of null or zero (0) will not trigger exceptions.
|
Specify the Severity, Data quality, a +/- absolute/percentage tolerance range, the last # of records over which the value needs to remain the same to be considered frozen, and Units to use See Notes below.
|
|
Frozen Value - Diff Pressure (Percentage) |
FrzVal DP Pct |
Gas Device |
||
|
Frozen Value - Energy (Absolute) |
FrzVal Energy Abs |
Gas Device |
||
|
Frozen Value - Energy (Percentage) |
FrzVal Energy Pct |
Gas Device |
||
|
Frozen Value - Mass (Absolute) |
FrzVal Mass Abs |
Gas Device |
||
|
Frozen Value - Mass (Percentage) |
FrzVal Mass Pct |
Gas Device |
||
|
Frozen Value - Static Pressure (Absolute) |
FrzVal SP Abs |
Gas Device |
||
|
Frozen Value - Static Pressure (Percentage) |
FrzVal SP Pct |
Gas Device |
||
|
Frozen Value - Temperature (Absolute) |
FrzVal Temp Abs |
Gas Device |
||
|
Frozen Value - Temperature (Percentage) |
FrzVal Temp Pct |
Gas Device |
||
|
Frozen Value - Volume (Absolute) |
FrzVal Vol Abs |
Gas Device |
||
|
Frozen Value - Volume (Percentage) |
FrzVal Vol Pct |
Gas Device |
||
|
Frozen Value... validation rules (liquid devices): The system will validate that a device is not incorrectly reporting the same value for a specified number of records. A device repeatedly reporting the same value will be considered frozen. |
||||
|
Frozen Value - Accumulated Energy (Absolute) |
FrzVal Acc En Abs |
Liquid Device |
The system will validate that the reported data remains within a defined tolerance range for the specified number of records to be considered frozen. Records failing validation will generate an exception.
|
Specify the Severity, Data quality, a +/- absolute/percentage tolerance range, the last # of records over which the value needs to remain the same to be considered frozen, and Units to use See Notes below.
|
|
Frozen Value - Accumulated Energy (Percentage) |
FrzVal Acc En Pct |
Liquid Device |
||
|
Frozen Value - Base Density (Absolute) |
FrzVal Base Dns Abs |
Liquid Device |
||
|
Frozen Value - Base Density (Percentage) |
FrzVal Base Dns Pct |
Liquid Device |
||
|
Frozen Value - Density Pressure (Absolute) |
FrzVal Dns Prss Abs |
Liquid Device |
||
|
Frozen Value - Density Pressure (Percentage) |
FrzVal Dns Prss Pct |
Liquid Device |
||
|
Frozen Value - Density Temperature (Absolute) |
FrzVal Dns Temp Abs |
Liquid Device |
||
|
Frozen Value - Density Temperature (Percentage) |
FrzVal Dns Temp Pct |
Liquid Device |
||
|
Frozen Value - Gross Standard Volume (Absolute) |
FrzVal Gr St Vol Abs |
Liquid Device |
||
|
Frozen Value - Gross Standard Volume (Percentage) |
FrzVal Gr St Vol Pct |
Liquid Device |
||
|
Frozen Value - Gross Volume (Absolute) |
FrzVal Grs Vol Abs |
Liquid Device |
||
|
Frozen Value - Gross Volume (Percentage) |
FrzVal Grs Vol Pct |
Liquid Device |
||
|
Frozen Value - Indicated Volume (Absolute) |
FrzVal Ind Vol Abs |
Liquid Device |
||
|
Frozen Value - Indicated Volume (Percentage) |
FrzVal Ind Vol Pct |
Liquid Device |
||
|
Frozen Value - Mass (Absolute) |
FrzVal Mass Abs |
Liquid Device |
||
|
Frozen Value - Mass (Percentage) |
FrzVal Mass Pct |
Liquid Device |
||
|
Frozen Value - Meter Pressure (Absolute) |
FrzVal Mtr Prss Abs |
Liquid Device |
||
|
Frozen Value - Meter Pressure (Percentage) |
FrzVal Mtr Prss Pct |
Liquid Device |
||
|
Frozen Value - Meter Temperature (Absolute) |
FrzVal Mtr Temp Abs |
Liquid Device |
||
|
Frozen Value - Meter Temperature (Percentage) |
FrzVal Mtr Temp Pct |
Liquid Device |
||
|
Frozen Value - Net Standard Volume (Absolute) |
FrzVal Nt St Vol Abs |
Liquid Device |
||
|
Frozen Value - Net Standard Volume (Percentage) |
FrzVal Nt St Vol Pct |
Liquid Device |
||
|
Frozen Value - Observed Density (Absolute) |
FrzVal Obs Dens Abs |
Liquid Device |
||
|
Frozen Value - Observed Density (Percentage) |
FrzVal Obs Dens Pct |
Liquid Device |
||
|
Frozen Value - Sediment and Water Volume (Absolute) |
FrzVal S&W Vol Abs |
Liquid Device |
||
|
Frozen Value - Sediment and Water Volume (Percentage) |
FrzVal S&W Vol Pct |
Liquid Device |
||
|
Frozen Value - (Absolute) |
FrzVal Uncr Dns Abs |
Liquid Device |
||
|
Frozen Value - (Percentage) |
FrzVal Uncr Dns Pct |
Liquid Device |
||
|
Minimum Average - Diff Pressure (Absolute) |
Min DP Avg |
Gas Device |
For a gas device, the system will validate that the differential pressure historical average for the specified number of previous records does not go below a minimum threshold value. Records failing validation will generate an exception. Note: Differential Pressure values of null or zero (0) will not trigger exceptions. |
Specify the Severity, Data quality, a Minimum threshold value, the last # of records to consider, and Units to use See Notes below. |
Notes:
The # of records value means the number of contiguous records prior to the one that currently arrived for validation. If a device supports hourly data, then one hour equals one record. If the PM History span is one hour, and you want to specify an average of one day worth of data, specify "24" and the system will calculate an average of the last 24 records prior to the existing one. This number cannot be "0": a value of zero (0) generates a validation exception for every history record in the date range.
The +/- value defines the absolute or percentage tolerance range. This number cannot be "0": a value of zero (0) generates a validation exception for every history record in the date range. The exception is DP: for Differential Pressure, null or zero (0) tolerance values will not trigger exceptions.
Station Rules
The following table lists the available validation rule types for a single gas station record, and each rule's configuration options.
| Rule Type | Default Rule Name | Valid Node Categories | Description | Configuration Options |
|---|---|---|---|---|
|
Dynamic Station Run Ratio (Percentage) |
StaRun Dyn Ratio |
Gas Device |
The system will validate that the contributed volume of any single run does not vary from the percentage of the base run, beyond the specified percentage range tolerance. Records failing validation will generate an exception. Note: Typically a run is configured with a single meter assigned. Although multiple meters can be assigned to a run, the subsequent meters are used as check devices. Only the first meter is used for purposes of validating the station run ratio. |
Specify the Severity, Data quality, and a +/- range for the tolerance, expressed as a percentage value (%) Default value is 0 % Note: The percentage you specify is relative to the volume of the base run. |
|
Linked Station Comparison... validation rules: The system will validate that volume, energy, or mass values do not differ between linked stations within the specified tolerance range. Note: The station to which any Linked Station validation rule applies must be configured with a linked station. This is true for any Node to which the rule is assigned. |
||||
|
Linked Station Comparison - Energy (Absolute) |
LStaComp Energy Abs |
Gas Device |
The system will validate that the data values do not differ between linked stations within the specified absolute/percentage tolerance range. Records failing validation will generate an exception.
|
Specify the Severity, Data quality, a +/- range for the tolerance, and Units to use
|
|
Linked Station Comparison - Energy (Percentage) |
LStaComp Energy Pct |
Gas Device |
||
|
Linked Station Comparison - Mass (Absolute) |
LStaComp Mass Abs |
Gas Device |
||
|
Linked Station Comparison - Mass (Percentage) |
LStaComp Mass Pct |
Gas Device |
||
|
Linked Station Comparison - Volume (Absolute) |
LStaComp Vol Abs |
Gas Device |
||
|
Linked Station Comparison - Volume (Percentage) |
LStaComp Vol Pct |
Gas Device |
||
|
Station Run Comparison... validation rules: The system will validate that pressure or temperature values for devices in a station do not differ within the specified tolerance range. |
||||
|
Station Run Comparison - Static Pressure (Absolute) |
StaRun Comp Press |
Gas Device |
The system will validate that the pressure for devices in a station does not differ beyond the specified absolute tolerance. Records failing validation will generate an exception. |
Specify the Severity, Data quality, a Greater than value for the tolerance, and Units to use |
|
Station Run Comparison - Temperature (Absolute) |
StaRun Comp Temp |
Gas Device |
The system will validate that the temperature for devices in a station does not differ beyond the specified absolute tolerance. Records failing validation will generate an exception. |
Specify the Severity, Data quality, a Greater than value for the tolerance, and Units to use |
Gas Analysis Data Rules
The following table lists the available validation rule types for imported gas analysis data, and each rule's configuration options. These rules will be validated against Nodes that support gas analysis data.
| Rule Type | Default Rule Name | Valid Node Categories | Description | Configuration Options |
|---|---|---|---|---|
|
Change Limit... validation rules: The system will validate the value of the HVV to determine if it has changed from the value in the previous gas analysis record and, if so, if the change is within the specified tolerance; otherwise the value will be considered to be an "out of range" value. |
||||
|
Change Limit - HVV (As Delivered) (Fraction) |
Limit HVV As Del Frc |
Gas Device |
The system will validate that a change in Heating Value Volume (As delivered) from the previous gas analysis record is within the specified tolerance. |
Specify the Severity, a +/- range for the tolerance, and Units to use (fraction) |
|
Change Limit - HVV (As Delivered) (Percentage) |
Limit HVV As Del Pct |
Gas Device |
Specify the Severity, a +/- range for the tolerance, and Units to use (%) |
|
|
Change Limit - HVV (Dry) (Fraction) |
Limit HVV Dry Frc |
Gas Device |
The system will validate that a change in Heating Value Volume (Wet) from the previous gas analysis record is within the specified tolerance. |
Specify the Severity, a +/- range for the tolerance, and Units to use (fraction) |
|
Change Limit - HVV (Dry) (Percentage) |
Limit HVV Dry Pct |
Gas Device |
Specify the Severity, a +/- range for the tolerance, and Units to use (%) |
|
|
Change Limit - HVV (Wet) (Fraction) |
Limit HVV Wet Frc |
Gas Device |
The system will validate that a change in Heating Value Volume (Dry) from the previous gas analysis record is within the specified tolerance. |
Specify the Severity, a +/- range for the tolerance, and Units to use (fraction) |
|
Change Limit - HVV (Wet) (Percentage) |
Limit HVV Wet Pct |
Gas Device |
Specify the Severity, a +/- range for the tolerance, and Units to use (%) |
|
|
High/Low Limits... validation rules: The system will validate the value of the selected gas analysis data item, to determine if its value is within the high/low range specified; otherwise the value will be considered out of range and will trigger the exception process. |
||||
|
High/Low Limits - Carbon dioxide (Fraction) |
Limit CO2 Frc |
Gas Device |
The system will validate that data values of the selected type are within the specified range. Records failing validation are considered "high" or "low" values and will generate an exception.
|
Specify the Severity, a Low and High value for the limits, and Method to use (fraction or %, from the options in the drop-down menu)
|
|
High/Low Limits - Carbon dioxide (Percentage) |
Limit CO2 Pct |
Gas Device |
||
|
High/Low Limits - Ethane (Fraction) |
Limit Ethane Frc |
Gas Device |
||
|
High/Low Limits - Ethane (Percentage) |
Limit Ethane Pct |
Gas Device |
||
|
High/Low Limits - Helium (Fraction) |
Limit Helium Frc |
Gas Device |
||
|
High/Low Limits - Helium (Percentage) |
Limit Helium Pct |
Gas Device |
||
|
High/Low Limits - Hydrogen Sulfide (Fraction) |
Limit H2S Frc |
Gas Device |
||
|
High/Low Limits - Hydrogen Sulfide (Percentage) |
Limit H2S Pct |
Gas Device |
||
|
High/Low Limits - Isobutane (Fraction) |
Limit Isobutane Frc |
Gas Device |
||
|
High/Low Limits - Isobutane (Percentage) |
Limit Isobutane Pct |
Gas Device |
||
|
High/Low Limits - Isopentane (Fraction) |
Limit Isopent Frc |
Gas Device |
||
|
High/Low Limits - Isopentane (Percentage) |
Limit Isopent Pct |
Gas Device |
||
|
High/Low Limits - Methane (Fraction) |
Limit Methane Frc |
Gas Device |
||
|
High/Low Limits - Methane (Percentage) |
Limit Methane Pct |
Gas Device |
||
|
High/Low Limits - Nitrogen (Fraction) |
Limit Nitrogen Frc |
Gas Device |
||
|
High/Low Limits - Nitrogen (Percentage) |
Limit Nitrogen Pct |
Gas Device |
||
|
High/Low Limits - Oxygen (Fraction) |
Limit Oxygen Frc |
Gas Device |
||
|
High/Low Limits - Oxygen (Percentage) |
Limit Oxygen Pct |
Gas Device |
||
|
High/Low Limits - Propane (Fraction) |
Limit Propane Frc |
Gas Device |
||
|
High/Low Limits - Propane (Percentage) |
Limit Propane Pct |
Gas Device |
||
|
High/Low Limits - Gas Analysis Relative Density (Absolute) |
Limit GA Rel Densit |
Gas Device |
The system will validate that data values of the selected type are within the specified range. Records failing validation are considered "high" or "low" values and will generate an exception.
|
Specify the Severity, and a Low and High value for the limits (absolute value) |
|
High/Low Limits - Sample Base Pressure (Absolute) |
Sample BP |
Gas Device |
Specify the Severity, and a Low and High value for the limits (absolute value) | |
|
High/Low Limits - Sample Base Temperature (Absolute) |
Sample BT |
Gas Device |
Specify the Severity, and a Low and High value for the limits (absolute value) | |
|
High/Low Limits - Total Liquid Content (Absolute) |
Limit Total Liquid |
Gas Device |
Specify the Severity, and a Low and High value for the limits (absolute value) |
|
|
High/Low Limits - n-Butane (Fraction) |
Limit n-Butane Frc |
Gas Device |
The system will validate that data values of the selected type are within the specified range. Records failing validation are considered "high" or "low" values and will generate an exception.
|
Specify the Severity, a Low and High value for the limits, and Method to use (fraction or %, from the options in the drop-down menu)
|
|
High/Low Limits - n-Butane (Percentage) |
Limit n-Butane Pct |
Gas Device |
||
|
High/Low Limits - n-Decane (Fraction) |
Limit n-Decane Frc |
Gas Device |
||
|
High/Low Limits - n-Decane (Percentage) |
Limit n-Decane Pct |
Gas Device |
||
|
High/Low Limits - n-Heptane (Fraction) |
Limit n-Heptane Frc |
Gas Device |
||
|
High/Low Limits - n-Heptane (Percentage) |
Limit n-Heptane Pct |
Gas Device |
||
|
High/Low Limits - n-Hexane (Fraction) |
Limit n-Hexane Frc |
Gas Device |
||
|
High/Low Limits - n-Hexane (Percentage) |
Limit n-Hexane Pct |
Gas Device |
||
|
High/Low Limits - n-Nonane (Fraction) |
Limit n-Nonane Frc |
Gas Device |
||
|
High/Low Limits - n-Nonane (Percentage) |
Limit n-Nonane Pct |
Gas Device |
||
|
High/Low Limits - n-Octane (Fraction) |
Limit n-Octane Frc |
Gas Device |
||
|
High/Low Limits - n-Octane (Percentage) |
Limit n-Octane Pct |
Gas Device |
||
|
High/Low Limits - n-Pentane (Fraction) |
Limit n-Pentane Frc |
Gas Device |
||
|
High/Low Limits - n-Pentane (Percentage) |
Limit n-Pentane Pct |
Gas Device |
||
|
Source Consistency Check |
Source Consistency |
Gas Device |
The system will validate that the source of the gas analysis sample is consistent with the source configured in the associated Node properties. Records failing validation will generate an exception. |
Specify the Severity |
|
Sum of Gas Composition validation rules: The system will validate the total of the gas composition data items, to determine if the value is within the specified tolerance from 100%; otherwise the value will be considered out of range and will trigger the exception process. |
||||
|
Sum of Gas Composition (Fraction) |
Gas Comp Sum Frc |
Gas Device |
The system will validate that the gas composition total adds up to 100% within the specified tolerance. Records failing validation will generate an exception.
|
Specify the Severity, a +/- range for the tolerance, and Units to use (fraction) |
|
Sum of Gas Composition (Percentage) |
Gas Comp Sum Pct |
Gas Device |
Specify the Severity, a +/- range for the tolerance, and Units to use (%) |
|
Job Rules
The following table lists the available validation rule types for job records, and each rule's configuration options.
| Rule Type | Default Rule Name | Valid Node Categories | Description | Configuration Options |
|---|---|---|---|---|
|
Calibration Drift Threshold... validation rules: The system will validate the value of the selected job calibration item, over the specified set of contiguous calibration jobs, to determine if the set is within the high/low limit specified; otherwise (if the entire set exceeds the limit) the set of values is considered "out of range" and will trigger the exception process. |
||||
|
Calibration Drift Threshold - Diff Pressure High (Percentage) |
Calib Drift DP High |
Gas Device |
The system will validate that the change in calibration data values is below the defined high drift threshold (by percentage) for the specified number of contiguous calibration jobs. Records failing validation will generate an exception.
|
Specify a High (percentage) drift tolerance, and the # of records to consider See Notes below.
|
|
Calibration Drift Threshold - Static Pressure High (Percentage) |
Calib Drift SP High |
Gas Device |
||
|
Calibration Drift Threshold - Temperature High (Percentage) |
Calib Drift T High |
Gas Device |
||
|
Calibration Drift Threshold - Diff Pressure Low (Percentage) |
Calib Drift DP Low |
Gas Device |
The system will validate that the change in calibration data values is above the defined low drift threshold (by percentage) for the specified number of contiguous calibration jobs. Records failing validation will generate an exception.
|
Specify a Low (percentage) drift tolerance, and the # of records to consider See Notes below.
|
|
Calibration Drift Threshold - Static Pressure Low (Percentage) |
Calib Drift SP Low |
Gas Device |
||
|
Calibration Drift Threshold - Temperature Low (Percentage) |
Calib Drift T Low |
Gas Device |
||
|
Calibration Drift Range... validation rules: The system will validate the value of the selected job calibration item, over the specified set of contiguous calibration jobs, to determine if the set is within the drift range specified; otherwise (if the entire set is outside the range) the value will be considered "out of range" and will trigger the exception process. |
||||
|
Calibration Drift Range - Diff Pressure (Percentage) |
Calib Range DP |
Gas Device |
The system will validate that the change in calibration data values is within the defined drift range (by percentage) for the specified number of contiguous calibration jobs. Records failing validation will generate an exception.
|
Specify a +/- range for the drift tolerance, and the # of records to consider See Notes below.
|
|
Calibration Drift Range - Static Pressure (Percentage) |
Calib Range SP |
Gas Device |
||
|
Calibration Drift Range - Temperature (Percentage) |
Calib Range T |
Gas Device |
||
|
Number of Calibration Points... validation rules: The system will validate the number of calibration points present for the selected job and data type, to determine if the number in the report matches the value specified; otherwise the value will trigger the exception process. |
||||
|
Number of Calibration Points - Diff Pressure (Absolute) |
# Calib Points DP |
Gas Device |
The system will validate that the number of calibration points present in the job report matches the specified value. Records failing validation will generate an exception.
|
Specify the Number of points expected to be present
|
|
Number of Calibration Points - Static Pressure (Absolute) |
# Calib Points SP |
Gas Device |
||
|
Number of Calibration Points - Temperature (Absolute) |
# Calib Points Temp |
Gas Device |
||
Notes:
The High or Low drift threshold value defines the change tolerance by percentage. If this number is zero (0), the system detects drifts in value (either high or low, as applicable) and generates a validation exception when all (either high or low) records in the set are not of identical value.
The # of records value means the number of contiguous calibration jobs including the one that currently arrived for validation, therefore the value cannot be zero (0). In the event that a calibration test point value standard has been changed within the contiguous record range specified, the values will be ignored (no exceptions generated) until the specified number of calibration report records is generated within the span of the new point value standard.
The +/- value defines the tolerance range by percentage. If this number is zero (0), the system detects any drift in value and generates a validation exception when all records in the set are not of identical value.